Long story short--a UPS transitioning from line to battery makes most surge strips think it's a surge. They then cause (quite intentionally) a short. Bad for the UPS electronics. Do it often enough, and it's quite likely to cause a large enough short to blow both the surge strip and the UPS electronics.
A line-interactive and/or double-conversion UPS will take care of the spikes/surges. Only power bars (without surge protection) should be plugged into their load side.
Now, if you have a good UPS that puts out a true sine-wave (not an approximation, not pretty good, but an actual sine wave output), some of this does not apply. Unless you put the UPS on a bench and test it, make no assumptions that it's an actual sine-wave output.
Basically, square-wave output and stepped-wave output waveforms can make a surge strip think it's a surge/spike, and they short. That's bad for the UPS. Wikipedia sort of gets this right, but they don't really explain why (non sine-wave output waveforms are what cause the surge strip to go nuts and short).
this is the same reason you can not link up UPS units 'in line' to have hours of battery on a desktop pc, router, etc.